    Performing automated shutdown during a power failure using a USB-UPS with NUT - XCP-ng 8.2

    Scheduled Pinned Locked Moved Compute
    29 Posts 12 Posters 17.0k Views 13 Watching
    Loading More Posts
    • Oldest to Newest
    • Newest to Oldest
    • Most Votes
    Reply
    • Reply as topic
    Log in to reply
    This topic has been deleted. Only users with topic management privileges can see it.
    • H Offline
      Hannes_5253
      last edited by Hannes_5253

      @peek said in Performing automated shutdown during a power failure using a USB-UPS with NUT - XCP-ng 8.2:

      yum --enablerepo=* install nut.x86_64

      This video solved it for me (altough its in german)
      YouTube Tut

      Thread can be closed.

      1 Reply Last reply Reply Quote 0
      • olivierlambertO Offline
        olivierlambert Vates πŸͺ Co-Founder CEO
        last edited by olivierlambert

        Would you mind posting exactly the steps you did to make it work? That might be really helpful for the community πŸ™‚ (and maybe pushed to our official doc at some point!)

        H 2 Replies Last reply Reply Quote 1
        • okynnorO Offline
          okynnor
          last edited by okynnor

          I was able to make NUT work with XCP-NG. I used and followed the instructions in this post.

          On issuing the command:

          [21:56 xenserver1 ups]# ./xen-shutdown.sh 
          

          All VMs shutdown EXCEPT for the Xen Orchestra. I tried remove and reinstall Xen Tools

          apt install xe-guest-utilities
          

          I'm on Ubuntu 18.04

          Is there something that should be done with Xen Orchestra? Like I said, all other VMs shutdown quickly and properly. I only have Ubuntu 18.04 and one instance of FreePBX. FreePBX shutdown properly too.

          Update: it seems that after 5-10 minutes (not sure yet as I haven't timed it), the entire XCP-NG does shutdown but not sure if it was a forced of graceful shutdown on the VM running XO.

          1 Reply Last reply Reply Quote 0
          • H Offline
            Hannes_5253 @olivierlambert
            last edited by Hannes_5253

            @olivierlambert Oh man, only saw this answer because I went back to my old post. I will do a full guide when I have some time and send it to you.

            1 Reply Last reply Reply Quote 2
            • H Offline
              Hannes_5253 @olivierlambert
              last edited by Hannes_5253

              @olivierlambert
              I wrote down the to-dos. You can use it for the official docs if you like! When you have questions, just answer on this Post.

              Network UPS Tools
              Installation on XCP-ng Host

              At first: Connect your UPS.
              Then run this commands to install NUT:

              yum update
              
              yum –enablerepo=* install epel-release
              
              yum install nut
              
              yum install nut-client
              
              cd /etc/ups
              
              wget https://github.com/serrc-techops/NUT-Configuration/blob/master/slave/xen/xen-shutdown.sh
              
              chmod +x xen-shutdown.sh
              

              Important Commands

              • upsc apcups (check UPS connection)

              • systemctl restart nut-server
                (NUT-server reboot) | (Use this to apply configuration changes and to connect the UPS after System startup)

              • systemctl restart nut-monitor (NUT-monitor restart)

              • nut-scacnner -U (shows connected devices)

              Configure the files stored in /etc/ups like this:
              upsmon.conf

              RUN_AS_USER root
              MONITOR apcups@localhost 1 admin [PASSWORD] master
              SHUTDOWNCMD β€ž/etc/ups/xen-shutdown.shβ€œ
              

              nut.conf

              MODE=netserver
              

              ups.conf

              pollinterval = 1
              maxretry = 3
              [apcups]
              driver = usbhid-ups 
              #->when you use USB devices
              port = auto
              desc = β€ž[NAME]β€œ
              vendorid = [VENDORID]
              productid = [PRODUCTID]
              serial = β€ž[SERIALNO]β€œ
              

              upsd.conf

              LISTEN 0.0.0.0 3493
              

              upsd.users

              [admin]
              password = [PASSWORD]
              actions = set
              actions= fsd
              instcmds = ALL
              

              Finish config Changes

              systemctl restart nut-server
              systemctl restart nut-monitor
              

              Finished
              Good to know: You can now also connect to your NUT server via the pfSense plugin by using the credentials in uspd.users to have a gui for your UPS. To do this you have to open up Port 3493 on your host.
              Run this command to open the Port:

              iptables -I INPUT -p tcp -m tcp --dport 3493 -j ACCEPT
              

              Then save your changes to a config file and adjust Year, Month and Day in the config name. In my case it's the 22th of december in 2022:

              iptables-save > /etc/sysconfig/iptables
              mkdir /etc/iptables/
              iptables-save > /etc/iptables/rules_2022-12-22_INPUT_ACCEPT_3493_NUT.v4 --> Optional, extra saving for Backups.
              

              I recommend using this convention of naming your rule files. Its a lot easier to track your changes and to restore files.

              lkniteL 1 Reply Last reply Reply Quote 3
              • lkniteL Offline
                lknite @Hannes_5253
                last edited by lknite

                @Hannes_5253 awesome! Thank you for this posting, it's helping me to get a nut client installed. Note for folks coming across this later I needed to use the following to install the nut-client:

                yum -y install nut-client --enablerepo=epel
                

                It would be cool if xcp-ng came pre-installed with nut-client and a default configuration that shuts down the xen server & turns off the ups after it finishes shutting down... similar to how truenas has a service which can be enabled to do so. You'd have to configure it of course, with the nut server to monitor, credentials, and some other options such as whether to actually powerdown the ups after shutting down or not, but maybe through a nice gui after turning it on. Seems like everyone should be using this setup ... just a matter of time till they are ready to.

                Another reason this would be nice to be integrated, is that docs recommend setting up a user account for nut, one for the monitor so clients can access and another for the shutdown so one of the watchers doesn't change the shutdown script & nut provides a file that indicates when the ups should shutdown, so having that be the same on all xcp-ng systems rather than custom solution would be good.

                H 1 Reply Last reply Reply Quote 3
                • H Offline
                  Hannes_5253 @lknite
                  last edited by Hannes_5253

                  @lknite Glad I could help and I agree. πŸ‘πŸ»

                  1 Reply Last reply Reply Quote 0
                  • olivierlambertO Offline
                    olivierlambert Vates πŸͺ Co-Founder CEO
                    last edited by olivierlambert

                    Hi,

                    Sadly, this use case is more meant for "non server-grade", where your machine isn't hosted in a datacenter (which is the default XCP-ng target/market).

                    However, I'm not against helping people doing the configuration or having an official guide to document it (I mean, in our doc)

                    Keep in mind we are always trying to find a balance between maintaining something (meaning time+money over other features) vs where the money is coming from (companies paying for support). If we pre-install all of this, it means we'll need to maintain it, while we still have a huge backlog of critical feature for our main (paying) target πŸ™‚ I hope you understand. Also, if we succeed and continue to grow that way with a far larger team than today, we could probably use that extra money from companies to improve integrations for the rest. But before doing it, we need to focus.

                    2b2bff2 1 Reply Last reply Reply Quote 2
                    • 2b2bff2 Offline
                      2b2bff @olivierlambert
                      last edited by

                      @olivierlambert I wonder how datacenters are doing this then in case of power loss? Or isn't that something of their concern?

                      1 Reply Last reply Reply Quote 1
                      • olivierlambertO Offline
                        olivierlambert Vates πŸͺ Co-Founder CEO
                        last edited by olivierlambert

                        In a DC, you have usually 2x power feed per rack (one on the left, one on the right). So even if one power line/feed is down, it's not a problem, since all your machines are usually dual PSU.

                        Also, everything is backed by UPS (both feeds) inside the building, and then diesel generators are taking the load after 10/15 minutes (diesel takes few minutes to start).

                        So in a colo, you will never have to get your own UPS.

                        2b2bff2 1 Reply Last reply Reply Quote 1
                        • 2b2bff2 Offline
                          2b2bff @olivierlambert
                          last edited by

                          @olivierlambert in simple words: they just don't shut down. And if they would have to there are bigger problems to solve.
                          Thanks for answering...

                          gskgerG 1 Reply Last reply Reply Quote 1
                          • gskgerG Offline
                            gskger Top contributor @2b2bff
                            last edited by gskger

                            @2b2bff I think that there are still some business scenarios, where this functionality would come in handy.

                            For example, we are running server rooms at our main production sites worldwide (no data centers, no colo, all on-site). Each features a three VMware hosts cluster with shared storage, backup, switches, and firewalls in an air-conditioned server room with adequate fire prevention/protection. All have two power feeds (A and B or left and right as Olivier called them) and all systems have dual PSUs, but the sites usually have only one power supplier and no generators.

                            Feed A goes to an UPS and feed B directly to the power line. If the power goes down, the UPS automatically triggers the vCenter, storage and backup to shut down when the UPS remaining runtime is below a certain threshold.

                            But I can perfectly understand Oliviers reasoning and there are workarounds. It all depends on your risk appetite (if that is a word in English).

                            2b2bff2 1 Reply Last reply Reply Quote 0
                            • 2b2bff2 Offline
                              2b2bff @gskger
                              last edited by

                              @gskger yeah same on my place. I play around with xcp-ng at home, where this is not important, and there is no UPS. So it is not important here.
                              But I have built two hosts at work in a server room as well. Together with TrueNAS and a couple of other things. The APC UPS has a management card, so it can be reached via network, but somehow the hosts have to shut down gracefully if needed. That's how I stumpled upon this thread in the first place.

                              1 Reply Last reply Reply Quote 1
                              • olivierlambertO Offline
                                olivierlambert Vates πŸͺ Co-Founder CEO
                                last edited by

                                I'm not saying it's not important in general (it depends on the use cases) πŸ™‚ But in our priorities (the "regular" DC world), it is not. For the "Edge computing" case, it might be more important, but the word "focus" doesn't have any meaning if we do everything at the same time.

                                And as usual, contributions are always welcome!

                                1 Reply Last reply Reply Quote 2
                                • O Offline
                                  odeawan
                                  last edited by

                                  Would just having the nut client be sufficient enough on the base XCP-NG to tigger a shutdown via NUT? Maintaining the NUT server seems to be a hold up and add extra complexity for XCP-NG. We all may have different DC power situations, but we could all use tools in our belt at home or the data center.

                                  H 1 Reply Last reply Reply Quote 0
                                  • H Offline
                                    Hannes_5253 @odeawan
                                    last edited by

                                    @odeawan Sure but you need a nut server. When you use the XCP-NG Server as a client you have to install the nut server on a different system. You can't install the nut server on a vm on the same host because the nut server must be installed on a system to shut down last.
                                    So running this scenario is the most redundant and efficient way.

                                    1 Reply Last reply Reply Quote 0
                                    • O Offline
                                      odeawan
                                      last edited by

                                      Well I still don't think it is out of scope then for just the NUT client for enterprises or HomeLabs on XCP-NG.

                                      SBCs are everywhere these days. Using a Raspberry Pi as the NUT Server in a homelab or a flavor of a more robust server for NUT seems like a solid choice. No USB passthrough to worry about, uptime on a 1500VA+ UPS, forget about it! There are a handful of guides how to get it running for a Pi or anything else (including this post).

                                      As I think this though, I would still feel ok with another external device watching, waiting, and notifying me on a successful power off of any number of my hosts and VMs. Not all enterprises or homelabs can afford (even if their appetites want it) to get enterprise level power automations. We have our power. Break the chain. @olivierlambert

                                      1 Reply Last reply Reply Quote 0
                                      • olivierlambertO Offline
                                        olivierlambert Vates πŸͺ Co-Founder CEO
                                        last edited by olivierlambert

                                        Which chain? The development is open, if you want something, do it πŸ™‚ If you want to be the maintainer so we can have it updated, packaged and put in our repo (even if not bundled by default), go ahead! If we think there's people behind it, we are not against, since it's an extra package.

                                        D 1 Reply Last reply Reply Quote 4
                                        • D Offline
                                          dj423 @olivierlambert
                                          last edited by dj423

                                          This post is deleted!
                                          1 Reply Last reply Reply Quote 0
                                          • N Offline
                                            nomad
                                            last edited by

                                            After NUT's grand reconfiguration there are a few things that you need to be aware of:

                                            In order to run NUT as a monitor to shut down your XCP-ng hypervisors it is no longer sufficient to just install nut-client and enable nut-monitor.

                                            You also need to install nut and enable nut.target or nut-monitor won't autostart. There won't be anything in journalctl either, since it isn't even trying to start - the thing that tells it to do so is the nut.target and if that's missing nothing will ever trigger.

                                            yum install nut nut-client --enablerepo=epel
                                            

                                            make your edits in nut.conf and upsmon.conf then

                                            systemctl enable nut.targetΒ 
                                            systemctl enable nut-monitorΒ 
                                            systemctl start nut-monitor
                                            
                                            C 1 Reply Last reply Reply Quote 0